Electrician Breaker question

PickettSFHunter

Well-Known Member
Joined
Jan 11, 2004
Messages
21,113
Location
Jamestown, TN
My electrical panels are ready to get started finishing out. What I am being told is that code no longer allows for the 20 amp breakers like are in most homes that cost like $7. That i will have to have 20 amp dual purpose afci/gfci breakers at like $60 each 😯 for every breaker (about 25 of them) This seems to be the case but just wanted to ask here. Of course everything just has to be insanely expensive instead of going for $7 ones like every house I’ve ever been in 😂
 

Specializedjon

Well-Known Member
Joined
Feb 25, 2019
Messages
5,619
Location
Middle TN
Your local codes will trump everything I say, but...20 amp GFCI are only required near a water source (sinks, etc.). I've never heard of dual purpose 20 amps being required for all the breakers. You can also reference the NEC (National Electrical Code) to get more information on residential applications. MOST jurisdictions adhere to the national code. I've build several hundred panels in my day and I've never used GFCI's unless the load side (receptacle) was near sinks, pools, outdoor BBQ's, etc.
 

DMD

Well-Known Member
Joined
Jan 16, 2006
Messages
8,013
Location
East TN
Your local codes will trump everything I say, but...20 amp GFCI are only required near a water source (sinks, etc.). I've never heard of dual purpose 20 amps being required for all the breakers. You can also reference the NEC (National Electrical Code) to get more information on residential applications. MOST jurisdictions adhere to the national code. I've build several hundred panels in my day and I've never used GFCI's unless the load side (receptacle) was near sinks, pools, outdoor BBQ's, etc.
I'm not an electrician, but that's all I've ever known. Only near a water source.
 

Crappieaddict

Well-Known Member
Joined
Dec 8, 2017
Messages
3,024
Location
Blount County, TN
My electrical panels are ready to get started finishing out. What I am being told is that code no longer allows for the 20 amp breakers like are in most homes that cost like $7. That i will have to have 20 amp dual purpose afci/gfci breakers at like $60 each 😯 for every breaker (about 25 of them) This seems to be the case but just wanted to ask here. Of course everything just has to be insanely expensive instead of going for $7 ones like every house I’ve ever been in 😂
Our cabin was finished about two years ago, and we were told that this in now required to pass inspection.
 

Specializedjon

Well-Known Member
Joined
Feb 25, 2019
Messages
5,619
Location
Middle TN
Commercial receptacles are now required by code to be "upside down" (ground at the top). Why you ask? So if a picture falls off a wall or something hits the cord that's plugged into the receptacle, it will break ground first.

Geniuses running the show. Ugh.
 

ImThere

Well-Known Member
Joined
Aug 24, 2006
Messages
13,415
Location
Lewisburg, Tn
thats what the NEC was changed to but tennessee was amended in 2018 to include only bedrooms.

you need to call your local inspector and see what his requirement is as he has authority in the NEC to make changes.
This
 

Specializedjon

Well-Known Member
Joined
Feb 25, 2019
Messages
5,619
Location
Middle TN
thats what the NEC was changed to but tennessee was amended in 2018 to include only bedrooms.

you need to call your local inspector and see what his requirement is as he has authority in the NEC to make changes.
Have a $50 bill in the palm of your hand when you shake his hand. Works wonders 😂
 

backyardtndeer

Well-Known Member
Joined
Jul 29, 2015
Messages
13,179
Location
West Tennessee
I cannot speak to current code, but I can tell you that you can look up the current codes online. I bought a book on 2009 nec when I built my house. At that time arc faults were required for ALL living spaces and ground faults for all potential wet spaces. The amperage of the receptacle being 20 amps is irrelevant, if it is in a living space. Kitchen required 2 separate ground fault circuits. I wired a dedicated 20 amp line to the fridge that was not Gfci.
 

ImThere

Well-Known Member
Joined
Aug 24, 2006
Messages
13,415
Location
Lewisburg, Tn
My electrical panels are ready to get started finishing out. What I am being told is that code no longer allows for the 20 amp breakers like are in most homes that cost like $7. That i will have to have 20 amp dual purpose afci/gfci breakers at like $60 each 😯 for every breaker (about 25 of them) This seems to be the case but just wanted to ask here. Of course everything just has to be insanely expensive instead of going for $7 ones like every house I’ve ever been in 😂
Btw when we were going to replace the electrical panel in our other home, we were told exact same thing you were
 

Madbowh

Well-Known Member
Joined
Sep 30, 2020
Messages
354
Location
Cumberland County
Call your electrical inspector and ask for a consultation appointment, they'll gladly do it and answer any questions you have and tell you what they will pass.

This is code in most places now, I'm a fan of running 20 amp 12 ga wire. But you also should consider what you'll actually be pulling. In a bedroom 15amp is fine. Bathroom you'll probably want the 20amp kitchens for sure.

Possibly living room depending on what your using tv, couple game systems, cable box, surround sound(really depends on this one) my surround with sub is only 100w.
 

DaveTN

Well-Known Member
Joined
May 4, 2006
Messages
5,768
Location
Middle Tennessee
Local codes come into play. When I needed some electrical work done I leaned that not only am I required to use an electrician licensed by the state of Tennessee, but one that is also licensed by the city of Murfreesboro.
 

Madbowh

Well-Known Member
Joined
Sep 30, 2020
Messages
354
Location
Cumberland County
If your set on using 12ga/20amp breakers go buy them yourself tell your electrician to install after inspection is done swap them out yourself for regular 20amp breakers and return them. Many many houses just have regular 20amp breakers.
 

WTM

Well-Known Member
Joined
Oct 16, 2008
Messages
13,938
Location
benton co.
Have a $50 bill in the palm of your hand when you shake his hand. Works wonders 😂

yeah back when bennie akers was our local inspector i imagine a lot of that went on. but then again several houses burned because of improperly wired door bell transformers of all things.

when billy replaced him all of that went away and billy was flunking wuite a few.
 

jlanecr500

Well-Known Member
Joined
Jul 16, 2015
Messages
2,321
I built one of our houses in 2010 and most 20a breakers are either afci or gfci. I didn't have to but that little investment can be the only thing that prevents a fire. As seen on this site, outlets fail and afci's will detect the arcing and open up.

In my current build/ remodel, all 20a breakers will be dual function afci/gfci breakers. I use only seimens panels and their new ones have plug on neutral bars. I bought the breakers for $30 each. You just have to look for deals. The only 15a breaker will be for the smoke alarm system.

I never use gfci outlets after seeing what can happen to them.

Electrical is one thing not to cheap out on.
 